Should a 9.5kw leccy shower always run it's own cable into a seperate fuse/trip switch in junction box ? 
 
At moment 
 
Electric shower (don't know KW), the wiring comes from the shower into a pull switch on roof and then down to leccy box...Now as far as I can see it is not controlled in the box by a seperate fuse / trip switch. 
 
Bought a new shower (9.5kw) and on instructions says it should be on a seperate cable and into a seperate trip / fuse of it's own..Or the circuit could heat up. 
 
So is this really neccesary when it goes through the switched pull cord in bathroom.. 
 
I am assuming the shower at moment just runs through the ring main of the house as there is no seperate trip / fuse for it...there is seperate fuses for all the heaters and the hot water etc.. 
 
So do i need an electrician out to fit a new wiring from shower down into box and seperate fuse / switch? 
 | 
smcGSI16V 
Member 
 
Registered: 26th May 03
 Location: Farnborough  Drives: Thurlby 888 CDTi No.98 
User status: Offline 
 
 | 
 
When ever we installshoers at work they are to their own mcb/fuse. 
 
I would if I was you,  better safe than sorry.
 | 
Leighton 
Member
 
Registered: 21st Feb 01
 Location: Liverpool 
User status: Offline 
 
 | 
 
yep should be on its own fuse  
normaly the same size as electric ovens, dont just use a normal 32 amp one
 | 
mattk 
Member 
 
Registered: 27th Feb 06
 Location: St. Helens  
User status: Offline 
 
 | 
 
Id put it into your consumer unit on a seperate RCD, showers need to be 10mm cable to 
 | 
AK 
Member 
 
Registered: 5th Jul 00
 Location: Aberdeen City 
User status: Offline 
 
 | 
 
10mm cble... 
 
feckin expensive and a ball ache to work with  
 | 
coupe_babe 
Member 
 
Registered: 27th Jun 07
 
User status: Offline 
 
 | 
 
10mm cable, MUST be on its own circuit, protected by an RCD or MCB at the very least.  
The pull cord is just an isolator, you still need this aswell as the MCB/RCD as the pull cord doesnt offer short circuit/overload protection.  
 
I would be very surprised if your current shower isnt on its own circuit. 
 
 | 
mattk 
Member 
 
Registered: 27th Feb 06
 Location: St. Helens  
User status: Offline 
 
 | 
 
quote: Originally posted by AK 
feckin expensive and a ball ache to work with   
   
 
sparks always say this to us too, try working with 28mm copper!
 | 
GT4Brody 
Member 
 
Registered: 26th Sep 01
 Location: south 
User status: Offline 
 
 | 
 
10mm t and e rcd protected with 45amp double pole pull cord. 
9.5kw draws a lot of current so correct size cable is very important.
 | 
Tom J 
Organiser: South Wales Premium Member 
 
Registered: 8th Sep 03
 Location: Bridgend 
User status: Offline 
 
 | 
 
thought of changing it for a manual thermostatic shower?
 | 
mav 
Member 
 
Registered: 19th Jun 01
 Location: Scotland 
User status: Offline 
 
 | 
 
Thanks for replies on this....The shower was run off a different trip and not in the ring main...Just the switch in the cupboard beside electrics but off to the side where i didn't see it... 
 | 
scottmmw 
Member 
 
Registered: 9th Aug 05
 Location: Brotton, Cleveland 
User status: Offline 
 
 | 
 
quote: Originally posted by GT4Brody 
10mm t and e rcd protected with 45amp double pole pull cord. 
9.5kw draws a lot of current so correct size cable is very important. 
   
 
 
9500w Divide by 230v = 41.3 amps.  just for anybody who might wanna work it out  
 | 
GT4Brody 
Member 
 
Registered: 26th Sep 01
 Location: south 
User status: Offline 
 
 | 
 
quote: Originally posted by scottmmw 
quote: Originally posted by GT4Brody 
10mm t and e rcd protected with 45amp double pole pull cord. 
9.5kw draws a lot of current so correct size cable is very important. 
   
 
 
9500w Divide by 230v = 41.3 amps.  just for anybody who might wanna work it out   
   
 
 
 |