corsasport.co.uk
 

Corsa Sport » Message Board » Off Day » House Day » advice, electrician, showers


New Topic

New Poll
  Subscribe | Add to Favourites

You are not logged in and may not post or reply to messages. Please log in or create a new account or mail us about fixing an existing one - register@corsasport.co.uk

There are also many more features available when you are logged in such as private messages, buddy list, location services, post search and more.


Author advice, electrician, showers
mav
Member

Registered: 19th Jun 01
Location: Scotland
User status: Offline
31st Oct 08 at 14:14   View User's Profile U2U Member Reply With Quote

Should a 9.5kw leccy shower always run it's own cable into a seperate fuse/trip switch in junction box ?

At moment

Electric shower (don't know KW), the wiring comes from the shower into a pull switch on roof and then down to leccy box...Now as far as I can see it is not controlled in the box by a seperate fuse / trip switch.

Bought a new shower (9.5kw) and on instructions says it should be on a seperate cable and into a seperate trip / fuse of it's own..Or the circuit could heat up.

So is this really neccesary when it goes through the switched pull cord in bathroom..

I am assuming the shower at moment just runs through the ring main of the house as there is no seperate trip / fuse for it...there is seperate fuses for all the heaters and the hot water etc..

So do i need an electrician out to fit a new wiring from shower down into box and seperate fuse / switch?
smcGSI16V
Member

Registered: 26th May 03
Location: Farnborough Drives: Thurlby 888 CDTi No.98
User status: Offline
31st Oct 08 at 16:36   View User's Profile U2U Member Reply With Quote

When ever we installshoers at work they are to their own mcb/fuse.

I would if I was you, better safe than sorry.
Leighton
Member

Avatar

Registered: 21st Feb 01
Location: Liverpool
User status: Offline
31st Oct 08 at 16:41   View Garage View User's Profile U2U Member Reply With Quote

yep should be on its own fuse
normaly the same size as electric ovens, dont just use a normal 32 amp one
mattk
Member

Registered: 27th Feb 06
Location: St. Helens
User status: Offline
31st Oct 08 at 17:31   View User's Profile U2U Member Reply With Quote

Id put it into your consumer unit on a seperate RCD, showers need to be 10mm cable to
AK
Member

Registered: 5th Jul 00
Location: Aberdeen City
User status: Offline
31st Oct 08 at 18:26   View User's Profile U2U Member Reply With Quote

10mm cble...

feckin expensive and a ball ache to work with
coupe_babe
Member

Registered: 27th Jun 07
User status: Offline
1st Nov 08 at 18:48   View User's Profile U2U Member Reply With Quote

10mm cable, MUST be on its own circuit, protected by an RCD or MCB at the very least.
The pull cord is just an isolator, you still need this aswell as the MCB/RCD as the pull cord doesnt offer short circuit/overload protection.

I would be very surprised if your current shower isnt on its own circuit.

mattk
Member

Registered: 27th Feb 06
Location: St. Helens
User status: Offline
1st Nov 08 at 18:50   View User's Profile U2U Member Reply With Quote

quote:
Originally posted by AK
feckin expensive and a ball ache to work with


sparks always say this to us too, try working with 28mm copper!
GT4Brody
Member

Registered: 26th Sep 01
Location: south
User status: Offline
2nd Nov 08 at 13:37   View User's Profile U2U Member Reply With Quote

10mm t and e rcd protected with 45amp double pole pull cord.
9.5kw draws a lot of current so correct size cable is very important.
Tom J
Organiser: South Wales
Premium Member


Registered: 8th Sep 03
Location: Bridgend
User status: Offline
7th Nov 08 at 11:58   View User's Profile U2U Member Reply With Quote

thought of changing it for a manual thermostatic shower?
mav
Member

Registered: 19th Jun 01
Location: Scotland
User status: Offline
25th Nov 08 at 05:03   View User's Profile U2U Member Reply With Quote

Thanks for replies on this....The shower was run off a different trip and not in the ring main...Just the switch in the cupboard beside electrics but off to the side where i didn't see it...
scottmmw
Member

Registered: 9th Aug 05
Location: Brotton, Cleveland
User status: Offline
25th Nov 08 at 18:52   View User's Profile U2U Member Reply With Quote

quote:
Originally posted by GT4Brody
10mm t and e rcd protected with 45amp double pole pull cord.
9.5kw draws a lot of current so correct size cable is very important.



9500w Divide by 230v = 41.3 amps. just for anybody who might wanna work it out
GT4Brody
Member

Registered: 26th Sep 01
Location: south
User status: Offline
27th Nov 08 at 10:14   View User's Profile U2U Member Reply With Quote

quote:
Originally posted by scottmmw
quote:
Originally posted by GT4Brody
10mm t and e rcd protected with 45amp double pole pull cord.
9.5kw draws a lot of current so correct size cable is very important.



9500w Divide by 230v = 41.3 amps. just for anybody who might wanna work it out



 
New Topic

New Poll

  Related Threads Author Forum Replies Views Last Post
any electricians/plumbers out there?? sxi boy Off Day 51 2407
23rd Oct 09 at 15:09
by Tiger
 
Alarms at Sextons Seirrah South Wales 12 603
17th Sep 04 at 16:58
by flameredcorsab
 
Fire!!!!! UPDATE AND PIC......!!!??!!! mav House Day 76 5608
10th Nov 06 at 10:18
by mav
 
electric shower IvIarkgraham House Day 30 1760
21st Jan 08 at 17:33
by IvIarkgraham
 
Ford Fiesta Wiper Fuses nathy_87 Help Zone, Modification and ICE Advice 2 388
8th Sep 08 at 15:54
by Fonz
 

Corsa Sport » Message Board » Off Day » House Day » advice, electrician, showers 29 database queries in 0.0116019 seconds