[quote][i]Originally posted by ash_corsa[/i] [quote][i]Originally posted by IvIarkgraham[/i] no its power or electric kerry - the wire is about 5 foot long so i can run about an 8.5kw on it according to some web site i found earlier [/quote] 5ft of cable?? From the CCU (fuse box) to the shower location is only 5ft? the 6mm cable will need to be replaced with 10mm to comply with regs, what size MCB / fuse is protecting the shower circuit?? 8.5kw will be pulling about 37A needs 40A MCB 9.5kw - 42A needs 50A MCB [/quote]